400 amp CT cabinet and disconnect

Status
Not open for further replies.

Ray Brooks

New member
Location
Raleigh, NC USA
We are looking to install a CT cabinet and 400 disconnect on the rear of a building for a new fit-up. The only space to mount the gear is over 80ft away. What is greatest distance I can mount the gear unfused from the trough? I think it is 25ft is that correct?
 
We are looking to install a CT cabinet and 400 disconnect on the rear of a building for a new fit-up. The only space to mount the gear is over 80ft away. What is greatest distance I can mount the gear unfused from the trough? I think it is 25ft is that correct?

Is this the only disconnect for the building? If so then you can go around the entire building as long as you stay on the outside. Once you enter the building the NEC says that you must have a disconnect as near as possible to the point of entry. Unless Raleigh has a specific distance then you need to follow the NEC.
 
BTW, here is NC's official stance on this issue

NORTH CAROLINA DEPARTMENT OF INSURANCE ENGINEERING DIVISION STATEMENT ON SECTION 230-70(a)

The Engineering Division of the Department of Insurance states its position relative to 230-70(a) NEC? as follows:

"Service entrance conductors routed from their point of entrance into the structure, to their point of attachment to the service enclosure a distance horizontally not more than twice the nominal width of the service enclosure and vertically not more than the greater of 5 feet or twice the nominal height of the service enclosure shall be considered to be in compliance with the requirements of 230-70(a) of the current National Electrical Code. Service entrance conductors may be routed in the most direct route or at right angles. Service entrance conductors in excess of these specified limits will not be allowed unless specifically authorized by special permission from the electrical inspector having jurisdiction to accommodate adverse site conditions which would not reasonably allow installation within this criteria."

By stating such interpretation, it is specifically not the intent of this Division to encourage the utilization of excessive lengths of service conductors when more direct routes are otherwise available; nor, to discourage local jurisdictions from allowing lengths beyond those specified when reasonable prudence and judgment would indicate reasonable necessity to accommodate safety or adverse site conditions. This Division will however render Code interpretations pertaining to 230-7 O( a) within these constraints and refer requests for special permission exclusively to the electrical inspector having jurisdiction .'

Original issue May 1991
Updated June 1994
 