You have to have ABC&N in each pipe, and the pipes have to be the same length (approximately). Is this a service or a feeder? If a service, you may not need a ground wire. (The grounded conductor is bonded to grounding electrodes at both ends.) If it is a feeder, you need a #3 ground in each pipe, not the #6 that you would use with a single run of 3/0.
More details please!
The only issue I could see, is if the neutral qualifies as a "current-carrying conductor".
Do you mean as in derating it per 310.15(B)(3)(a)? He said THHN, so you start at 225A before derating. 225 x 0.8 = 180, and 180 x 2 = 360. Per 240.4(B) the next higher standard breaker (as listed in 240.6) is allowed, so 400A ought to be ok.
There are lots of reasons the wiring might have been shot down, other than that it's in parallel. The lack of detail is preventing my mental telepathy from working on the inspector.
The install is good. It is being rejected because of ampacity. It is a feeder.