Copperclad
Member
- Location
- Merritt Island, FL USA
Hi everyone!
Im looking at a set of prints for a very large residence & detached garage.
On the one line, they show a 400 amp 1 phase service, which is fine. What has me bothered, is the fact they show (3) 200 amp load centers feeding off the main 400 amp gear. (1) 200a panel in garage, (1) 200a panel in the main house first floor, and (1) 200a panel in the main house second floor.
The load calculation came out to 78kva. which is fine for a 400 service , it just does not seem right to pull a potential 600 amps from a 400 amp service.
I have never bid on a residential job this big it may very well be the norm, I would much appreciate some input from some of you experts.
Thanks guys!