Hi All. I am using the new 2017 code and have a question of the size conductors I can use for a 400 amp residential service. Here is what I have
90 degree C Copper conductors
400 amp Single Family Service
Ambient Soil Temp of 70 degrees
Conductors have no more than 10' above grade.
Conductors in conduit
Paralleled conductors
Conductors supply entire dwelling load
As I understand using chapter 3,
Temp correction multiplier is 1.04
6 conductors in a raceway multiplier is .8
Single Family Service multiplier is .83
75 degree C terminations
using this info I come up with:
Applying the Service demand factor I only need an ampacity of 332 amps (400x.83) or parallel conductors with an ampacity of 166 amps.
Using 3/0 THWN from the 90 degree C column. it is good for 225 amps. Multiply that by 1.04 (225x1.04) for Ambient Temp Correction I get 234 amps
Then correcting for 4 to 6 conductors in a conduit I get (234x.8) which is 187.2 amps per 3/0 conductor
Parallel that, I get 374.4 amps.
and finally because I have 75 degree C terminations I have to use the 75 degree C column to find that I'm OK with 3/0 for the termination (75 degree C is 200 amps per termination or 400 amps). 2/0 would be OK if it had the ampacity.
Does anyone else agree or disagree?
Taking that further: If I terminate the underground portion using 90 degree C connections before the enclosures containing the 75 degree C breakers, and I use 2 conduits instead of 1. I think that allows me to use 1/0.
90 degree C Copper conductors
400 amp Single Family Service
Ambient Soil Temp of 70 degrees
Conductors have no more than 10' above grade.
Conductors in conduit
Paralleled conductors
Conductors supply entire dwelling load
As I understand using chapter 3,
Temp correction multiplier is 1.04
6 conductors in a raceway multiplier is .8
Single Family Service multiplier is .83
75 degree C terminations
using this info I come up with:
Applying the Service demand factor I only need an ampacity of 332 amps (400x.83) or parallel conductors with an ampacity of 166 amps.
Using 3/0 THWN from the 90 degree C column. it is good for 225 amps. Multiply that by 1.04 (225x1.04) for Ambient Temp Correction I get 234 amps
Then correcting for 4 to 6 conductors in a conduit I get (234x.8) which is 187.2 amps per 3/0 conductor
Parallel that, I get 374.4 amps.
and finally because I have 75 degree C terminations I have to use the 75 degree C column to find that I'm OK with 3/0 for the termination (75 degree C is 200 amps per termination or 400 amps). 2/0 would be OK if it had the ampacity.
Does anyone else agree or disagree?
Taking that further: If I terminate the underground portion using 90 degree C connections before the enclosures containing the 75 degree C breakers, and I use 2 conduits instead of 1. I think that allows me to use 1/0.