Customer currently has 200 amp service to house. Also has an out building 250 feet away where heavy equipment will be used. Wants a 400 service. At the new meter base, will the line going to the outbuilding be considered a feeder? Thinking I will need a 200A disco for it next to the meter base. Any help appreciated, of course my first 400 amp service is a little more complex.
2023NEC
The way you have it worded, it will be a feeder, you will be on the load side of your disconnect so its not a service to the out building.
Wants a new meter base with a disconnect beside it........need a 200A disco for it next to MB...
So, your feeder to the out building will be a feeder from the load side of the 200 A disco. The service conductors stop at the line terminals.
If run PVC, you'll need an EGC and grounding electrode, if available or ground rode or 3/4 rigid pipe.
If you put a disconnect at the out building it can be out side or immediately inside.
Side note; have you considered voltage drop? At that 250 ft. and "heavy equipment".
I suggest an SPD for your heavy equipment, likely to have some electronics.
Is this considered at a dwelling type location....customer has 200 A service to
house....
I don't know anything about your city electrical jurisdiction but first responders shall have an emergency disconnect or use the 200A disconnect to meet 230.85 rule and 230.85(E) (1) (2)
Marking.