rojay
Senior Member
- Location
- Chicago,IL USA
I came across a 120/240 volt single phase 400 amp service at a residential job yesterday. It was a typical back to back installation with a 320 amp meter and two 2” RMC 90’s terminating at 2 separate 200 amp MB panel boards via 3-3/0 service entrance conductors.
Along with the service entrance conductors in each raceway a supply side bonding jumper was pulled and terminated at bonding bushings at both ends of each raceway.
While an NEC allowed parallel path for neutral current already exists between the meter can and the service disconnects via the 2” RGC’s - is the addition of another parallel path via #4 SSBJ’s pulled with the service conductors technically a code violation or just a waste of money?
Along with the service entrance conductors in each raceway a supply side bonding jumper was pulled and terminated at bonding bushings at both ends of each raceway.
While an NEC allowed parallel path for neutral current already exists between the meter can and the service disconnects via the 2” RGC’s - is the addition of another parallel path via #4 SSBJ’s pulled with the service conductors technically a code violation or just a waste of money?