Our POCOs around here have always said their 400 amp service is really only 320 amps. Is that true only in my area ?
No, it's everywhere. 320A is for continuous use. There is a true 400A for continuous but for residential, they use 320A meter bases.Our POCOs around here have always said their 400 amp service is really only 320 amps. Is that true only in my area ?
A lever bypass meter socket for a residential service is rated for 320 amps continuous duty and is the largest single phase meter that our local PoCo will allow without a CT cabinet. I have installed larger residential services(400-600 Amp) but they all required large CT cabinets with the meter base mounted to the CT cabinet.Our POCOs around here have always said their 400 amp service is really only 320 amps. Is that true only in my area ?
Exactly.Volunteer engineer at habitat project questioned that the poco had only a 20KVA xfmer (yes twenty) feeding 4 housing units with 200A services each..
POCO said they would upsize if there were ever a problem, all units have electric stoves but gas heat and gas water heaters. No electric cars (yet).