Smart $ said:
The gist of 230.42(B) is that if one's service disconnect has a higher amperage rating than the minimum calculated load, the ampacity of the service entrance conductors must have an ampacity equal to or greater than the rating of the service disconnect.
When the calculated load is
less than the minimum service size, I would agree. Once you venture above the minimum size service, then you have satisfied 230.42 and 230.79.
Your service disconnecting means and service entrance conductors
are not less than the minimums.
Smart $ said:
Example: calculated load is approximately 325A per ungrounded conductor. One opts for a 400 amp service [disconnect]. The ampacity of the service entrance conductors must be 400A or greater.
I agree with the outcome, but 230.42(B) has no bearing on this determination. 230.90 exception 2 is what gives us this information. If we selected a 350A breaker in your example, then we could use conductors sized for 325A according to exception 2 of 230.90.
If you cannot stay within the confines of the exception, then you must follow the rule, which says that "Such protection shall be provided by an overcurrent device in series with each ungrounded service conductor that has a rating or setting not higher than the allowable ampacity of the conductor."
Smart $ said:
infinity said:
So one set of 500 Kcmil conductors with a 400 amp disconnect and a less than 380 amp calculated load is no good?
That's how I read it. I'm actually hoping someone will shoot it down, but until then...
I disagree. Unless the load calculation comes to less than 350A (the last size fuse or circuit breaker), then this would be compliant.
Any load calculation between 351A and 380A for the setup Trevor described would be compliant, IMO.