Re: 400 amp service with 2-200 sub panels
230.40 exception #3 allows for set of service entrance conductors to feed each building. There is no requirment as to what the building would be used for. It just allows for it. now since it is allowed 230.71 allows for 6 disconects for each set of service entrance cables but each set of disconects have to be grouped not all together as this would disallow the exception#3 in 230.40 but each set of disconects as they are required to be on or at the closest entrance to the building has to be grouped. Now I do agree with that a disconect on the building with the meter would be a danger to firemen as responding to a fire in this building they could mistakenly think the disconect is for that building and turn it off without knowing that there is still power in that building this is why I brought up the exception that allows him to run the SEC directly to the house and place the disconect there. as he would be required to install a means of disconect there anyway.
Exception No. 3: A single-family dwelling unit and a separate structure shall be permitted to have one set of service-entrance conductors run to each from a single service drop or lateral.
230.71 Maximum Number of Disconnects.
(A) General. The service disconnecting means for each service permitted by 230.2, or for each set of service-entrance conductors permitted by 230.40, Exception Nos. 1, 3, 4, or 5, shall consist of not more than six switches or sets of circuit breakers,
230.72 Grouping of Disconnects.
(A) General. The two to six disconnects as permitted in 230.71 shall be grouped