400 amp service

Status
Not open for further replies.

GerryB

Senior Member
Can a 400amp main lug panel with double lugs be fed from the meter main with two separate ser cables each one on a 200 amp breaker. So parallel ser and you need to throw 2 breakers to kill the panel

Sent from my SM-G930V using Tapatalk
 
Can a 400amp main lug panel with double lugs be fed from the meter main with two separate ser cables each one on a 200 amp breaker. So parallel ser and you need to throw 2 breakers to kill the panel

Sent from my SM-G930V using Tapatalk

Absolutely not.
 
240.8 Fuses or Circuit Breakers in Parallel. Fuses and
circuit breakers shall be permitted to be connected in parallel
where they are factory assembled in parallel and listed
as a unit. Individual fuses, circuit breakers, or combinations
thereof shall not otherwise be connected in parallel.
 
240.8 Fuses or Circuit Breakers in Parallel. Fuses and
circuit breakers shall be permitted to be connected in parallel
where they are factory assembled in parallel and listed
as a unit. Individual fuses, circuit breakers, or combinations
thereof shall not otherwise be connected in parallel.
Thanks for that reference, Smart $!
 