kriverswaters
Member
I am planning on installing a 400A 120\240V single phase service to a four-plex apartment complex. The four pack meter base will have four 100A breakers to feed each apartment. Acording to my code book and calculations, the service feeder can be in a 3" metal rigid conduit with 2ea. 600MCM copper cables for the ungrounded conductors and a 500MCM for the grounded (neutral)conductor. Each indivdual apartment can be installed with #2 copper for the ungrounded conductors and a #3 for the grounded (neutral)conductor. According to NEC Table 250.66, the grounding cable to the electrode for this service should be a 1/0 copper conductor and each apartment 100A panel should be fed with a #6 copper wire. Am I correct in what I have described?