John Valdes
Senior Member
- Location
- SC.
- Occupation
- Retired Electrician
I looked at a job today. The homeowner wants an upgrade from 200 Amp to 400 amp. There are 2 seperate structures connected by a breezeway. The existing buried service laterral is positioned where upgrading would be very difficult. I reccommended that he move the service to the garage where it would be a straight run from the POCO xfmr. One 50' trench. Then make the house main service panel a sub panel. I am pretty sure this would not be a violation? But the garage has no plumbing and I would have no water pipe to bond to. Must I have a water line or would 2 grounding electrodes be allowed. The home is piped in copper. The breezeway is only for appearance and is not over either structure door. However, the breezeway does share an overhead crawl space with both structures
Does anyone see any problem with my reccommendations?
ps......The homeowner would prefer a seperate meter for the garage and leave the house as is. But according to the AHJ, both structures are considered as one structure, therefore only one service drop is allowed?
Does anyone see any problem with my reccommendations?
ps......The homeowner would prefer a seperate meter for the garage and leave the house as is. But according to the AHJ, both structures are considered as one structure, therefore only one service drop is allowed?