400 amp

Status
Not open for further replies.

normbac

Senior Member
client needs to mount a 400 amp metered wall mount panel 200 feet from house and then feed house with a 400 amp load center, he was wondering if I could get a wall mount that also had distribution so he could feed his gate operator and lights at the front of his property. Do they make such a panel?
 

wireguru

Senior Member
Im sure they do but its going to be very expensive. Can you just tap off a small panel for the loads out there?
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
When I was an apprentice, the company I worked for ordered such a combo unit w/o getting any size specs.

I was sent to pick it up, and left it at the supply house, because it was as big as the hood of my truck and weighed a couple hundred pounds. It was somewhere around $500+.




Get some of those ilsco tap lugs and nipple over to a 100A MCB Panel.
 

220/221

Senior Member
Location
AZ
Run a circuit or two back to the gate along with the feeders.

Don't forget the low voltage conduit for the intercom/remote opener.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Im sure they do but its going to be very expensive. Can you just tap off a small panel for the loads out there?
That would be my thought. The 400 amp meter sockets they use here have bolt studs so a dounle barrel lug allowing you to tap off a panel at the meter should work,
 

ceb58

Senior Member
Location
Raeford, NC
Cuttler-Hammer and Sq D both make 400amp meter combo's.
They come with 1 200amp installed and you buy the other 200. They both have 100amp buss built in that has 8 spaces. The last C-H I bought was $450.00 + 80.00 for the other 200amp breaker. The last Sq D was around $680.00
 

wireguru

Senior Member
Cuttler-Hammer and Sq D both make 400amp meter combo's.
They come with 1 200amp installed and you buy the other 200. They both have 100amp buss built in that has 8 spaces. The last C-H I bought was $450.00 + 80.00 for the other 200amp breaker. The last Sq D was around $680.00


that wont work if he wants all 400amps to go to the house. He needs a 400amp feed through panel.
 

masterinbama

Senior Member
Could you set a 400 amp meter main with 2 200 amp breakers? Set one 200 amp feed through at the meter location and pull 2 200 amp feeders to the house one from the feed thru and one from the other other main feeding 2 200 amp panels at the house.
 
Status
Not open for further replies.