The system is 115Vac, 20A, 3P, 5W, 400Hz, I need to install 12 of them. Can I group this In conduit? What type of insulation required? Do I need to run ground wire In conduit?
Each of those is 3 phase, with a neutral required (treat it like a 208/120 wye branch circuit). That is 4 wires per item plus the equipment ground (which could be a metal conduit). Normally, you derate things a bit for 400Hz because of heat, and aluminum raceways are preferred. Use 90C wire but treat it as 60C (not a code requirement, but its what we do). Don't excessively bundle or push the derating for bundling. Putting 48 wires in a conduit wouldn't be the best way to do this... I'd put maybe 2 circuits in a conduit and waver between #12 versus #10 conductors. Do you know the actual load (nameplate amps) of the device and whether it is a intermittent load, or a continual max draw type of load?
What's more important, using one large conduit or using the minimal wire size?
How long of a run are we taking about? Can a sub-panel be close to the loads?
With that load, I'd use #12 wire but with only two circuits per raceway because of the additional heating effects at 400Hz.
With that load, I'd use #12 wire but with only two circuits per raceway because of the additional heating effects at 400Hz.
For derate purposes, it would technically be 6 current carrying conductors. The neutral doesn't count when all 3 phases are used with it unless the load is non-linear. So 80% derate instead of 70%.I see. Only 8 current carrying conductor per raceway.
For derate purposes, it would technically be 6 current carrying conductors. The neutral doesn't count when all 3 phases are used with it unless the load is non-linear. So 80% derate instead of 70%.
I would not derate for 400 Hz for this size wire. The charts I use dont show much loss of ampacity for #12 at 400 Hz.
Those are relatively short runs, so I'd suggest one conduit per receptacle box. 1/2" for two circuits, 3/4" for four.The run is between 10-30 ft. Using one large conduit is not important. I am new in the field. I though it is better design if you can put it in large conduit and to use junction box to spread it to where it needs to be.
I said I would not derate ampacity on wire of this size because of it being 400 Hz. You still have to derate for number of CCC. I dont have my spreadsheet handy but I dont think being 400 Hz significantly affects conductor ampacity until the wire size gets to be pretty big. Like #6.If I may ask, what chart do you use?
8ccc in one conduit using #12@ 60C x 0.70 gives us 17.5A, is that number of loss you got?