I have a 320a meter feeding one 400a panel with a connected load of 181 amps. The meter also feeds a 400a outside panel with a connected load of 216a. Both panels have a 4in conduit installed to them.
My question is can I size my wire useing the 90deg table and parallel 4/0 at 80%=328a as long as Im under the 75deg ampacity of 288a with my load?
I think I have to parallel 300mcm al at 80%=368 and round up.
My question is can I size my wire useing the 90deg table and parallel 4/0 at 80%=328a as long as Im under the 75deg ampacity of 288a with my load?
I think I have to parallel 300mcm al at 80%=368 and round up.