400 sub panel 200% Nuetral

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No you would need parallel 500 kcmil neutrals or 200% of the phase conductors. Also 500 kcmil cannot be used with a 400 amp OCPD on the secondary because the ampacity is only 380 amps.

Welcome to the Forum. :)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What about 240.4(B)?

Does not apply due to 240.21(C).

240.21(C) Transformer Secondary Conductors. A set of con-
ductors feeding a single load, or each set of conductors feed-
ing separate loads, shall be permitted to be connected to a
transformer secondary, without overcurrent protection at the
secondary, as specified in 240.21(C)(1) through (C)(6). The
provisions of 240.4(B) shall not be permitted for transformer
secondary conductors.

Informational Note: For overcurrent protection require-
ments for transformers, see 450.3.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
What is the neutral load? If the neutral load is not high than 500 kcm may be 200% but if they want 200% of the conductors then you would need to parallel as Trevor stated
 