The conductors feeding the VFD must be sized at 125% of the VFD max input amps at whenever your supply voltage is. On the output side, just go with 125% of the motor nameplate FLA, unless, like I said, they are doing something funky.
As an example of funkiness, often times to get around the torque/speed issues, they will use a dual voltage motor, in this case 400V IEC motors can often be internally connected in Delta instead of Wye and run at 230V. So if you use a 400V maximum output of the VFD, but wire the motor for 230V, then tell the VFD it is a 230V 50Hz motor, the VFD puts out 230V at 50Hz so that the motor gets its proper V/Hz ratio and can develop full rated torque, but can continue to increase the speed at that V/Hz ratio until they get to 400V, which would be 87Hz before the motor enters the Constant Power operating range. So they don't start losing torque until you go over 87Hz, rather that beginning at 50Hz. The thing about that is, the motor power is actually going to be higher by the same ratio. So if it was 10kW at 230V 50Hz, it is now going to be 17.3kW at 87Hz, and you would pick the conductor size based on 17.3kW 230V. 1HP = .746kW, so that motor went from 7-1/2HP to 13HP, so I would base the conductor size as if it was 15HP 230V.
That's why I said the details matter.