after sizing in sec 250 wire is tremendous, what type of bushing and lug can be used to accomplish this project
True but that only is allowed on service conductors or supply conductors on a SDS. If this is on the load side of the generator breaker they will need to be sized on 250.122 and 4000 amps which would be 500 KCMIL for every pipe.You can use individual bond jumpers to each bushing based on the conductor in that conduit
(Note 3 to 250.102(C))
Sounds good to me.When I saw "generator" I was thinking SDS but thanks for the reminder.
I am correct that one option would be to loop (1) 500 to multiple conduits, correct ?
Does anyone have a pic of 500 mcm attached to a bushings?after sizing in sec 250 wire is tremendous, what type of bushing and lug can be used to accomplish this project
I'll have to look I may have one. Why do you need bonding bushings?Does anyone have a pic of 500 mcm attached to a bushings?
You're using concentric knock outs? We just remove the factory lug if it's not large enough and replace it with the proper size.must be a bonding bushing
Yes. Could be a job spec but I agree it's sounding like they're not required. But even so the question is about using them so just swap out the lugs for larger ones.Would you care to give a little detail.
I think many of us are trying to picture a generator application that requires bond bushings especially with no concentric KOs