What do you think about a electric wall heater 4000 watts fed from a dedicated 12 guage 20 amp circuit?
Nec says continuous and I calculate 16.67 amps X 1.25% +20.84 amps can ypu still use a 20 amp circuit. I am seeing this quite often done. However does it comply if you replace with a new and different heater?
Thanks