I need to provide an underground supply from the utility transformer to a 4000A, 208/120V main switchgear, of a new construction hotel.
As of engineered drawings, the service should be provided with 10 sets of 600KCM parallel runs, CU.
Q: Considering none of both wire ends connect to OCP, but to termination lugs at XFMR side, and bus bars at main gear pulling section,
can I run 9 sets of 600KCM or maybe 10 sets of 500KCM instead? and save some $$ in copper.
or maybe better run 10 sets of 700KCM AL?
cable pulls are about 250ft
Jorge
As of engineered drawings, the service should be provided with 10 sets of 600KCM parallel runs, CU.
Q: Considering none of both wire ends connect to OCP, but to termination lugs at XFMR side, and bus bars at main gear pulling section,
can I run 9 sets of 600KCM or maybe 10 sets of 500KCM instead? and save some $$ in copper.
or maybe better run 10 sets of 700KCM AL?
cable pulls are about 250ft
Jorge