cobrahead
Member
- Location
- Fort Worth
Going from CT/transocket to a 400A fusible disconnect (Square D D325NR) to 400A panel with main breaker inside shop. Single lug per phase in disconnect are rated for (max) 600 kcmil or (max) 2ea 250 kcmil. Note on service disconnect enclosure says not enough room to bend larger than 250 kcmil inside enclosure. Lugs are 'suitable' for 75C conductors.
Dual lugs per phase in CT accept (max) 600 kcmil on each.
I plan to go straight out the top of the CT with dual 3" conduits to a wire way that is 8" x 8" x 48" and then out of the wire way straight down into the disconnect with dual 3" conduits. I also plann to use parallel 250 kcmil CU THHN on all phases and neutral.
Does that sound about right? Overkill anywhere? missing something entirely?
Thanks