Hello all, I have a 400a 3ph 4w 480v UG service - my service conductors are terminating in a self contained meter & then fed from there to the adjacent service disconnect switch.
The AHJ wants a grounding electrode conductor termination in the meter can.
My question would be can I terminate the grounding electrode conductor from my ground rods to the neutral bar in meter can (factory bonded to can) & then terminate the grounding electrode conductor coming from the main ground bar in the building (ufer, fire sprinkler, step down transformers etc) to the service disconnect neutral bar (bonded to can).
Thanks.
The AHJ wants a grounding electrode conductor termination in the meter can.
My question would be can I terminate the grounding electrode conductor from my ground rods to the neutral bar in meter can (factory bonded to can) & then terminate the grounding electrode conductor coming from the main ground bar in the building (ufer, fire sprinkler, step down transformers etc) to the service disconnect neutral bar (bonded to can).