400a ATS for 2 200a panels

Status
Not open for further replies.

TJon40's

Member
Location
Texas
Occupation
Electrician
I have looked around and only found a couple 400a split 200a srevice entrance rated transfer switches, the Briggs and Stratton and Milbank. The Briggs and Stratton says it must be used with their generators, and the Milbank looks too busy inside from the factory. I am limited on space so installing 2 200a switches is out. The generator will be a used 50kw diesel Kholer. Kholer makes 400a ser ats with double lugs on the load side, would that be the way to go, or am I getting into 240.21?
 
I have looked around and only found a couple 400a split 200a srevice entrance rated transfer switches, the Briggs and Stratton and Milbank. The Briggs and Stratton says it must be used with their generators, and the Milbank looks too busy inside from the factory. I am limited on space so installing 2 200a switches is out. The generator will be a used 50kw diesel Kholer. Kholer makes 400a ser ats with double lugs on the load side, would that be the way to go, or am I getting into 240.21?
If it has overcurrent protection then likely yes 240.21 will be applied. Might not really be that big of an issue for you depending on arrangement of items. You basically have a 10 foot rule a 25 foot rule and outside taps of unlimited length to contend with.
 
Do ATS's need to have load shedding to prevent overloading the gen or is that just for critical wiring?
 
Do ATS's need to have load shedding to prevent overloading the gen or is that just for critical wiring?
some do some don't. Often it is just relay contacts to control the load being shed and additional wiring is necessary to get things done.
 
If it has overcurrent protection then likely yes 240.21 will be applied. Might not really be that big of an issue for you depending on arrangement of items. You basically have a 10 foot rule a 25 foot rule and outside taps of unlimited length to contend with.

The transfer switch would be right next to the meter base with a nipple and then a gutter underneath the two to feed the 200's. The 400a breaker on the ATS would be the overcurrent protection for the 2 200a panels and the grounds and neutrals will be separated in the 200's.
 
The transfer switch would be right next to the meter base with a nipple and then a gutter underneath the two to feed the 200's. The 400a breaker on the ATS would be the overcurrent protection for the 2 200a panels and the grounds and neutrals will be separated in the 200's.
Feeder tap rules would apply, but shouldn't really make you change what you would otherwise do in your situation.
 
Do ATS's need to have load shedding to prevent overloading the gen or is that just for critical wiring?
They do if the transfer switch is automatic and the total load exceeds the output of the generator. 702.4(B)(2).
 
They do if the transfer switch is automatic and the total load exceeds the output of the generator. 702.4(B)(2).

That’s what I was getting at. The generator is rated for 208amps and feeds two-200a panels with an automatic transfer switch


Sent from my iPhone using Tapatalk
 
That’s what I was getting at. The generator is rated for 208amps and feeds two-200a panels with an automatic transfer switch


Sent from my iPhone using Tapatalk
But is your total load calculation over 208 amps? Just because you have 400 amps worth of mains doesn't necessarily mean you are anywhere close to 400 amps of load being all that possible.
 
Either way wouldn't he have to split it back to 2 separate 200amp breakers after his 400 ATS? Because the feeders (SER, etc.) are longer than tap rules (I assume) and are probably only 3/0 copper or equivalent. I'm just curious how you could put OCPD at 400amps on 3/0 copper.
 
My own personal house has essentially the METER feeding a 400 disconnect and then a Generac HTS (400A ATS). My "main" panel is a 400A subpanel. This feeds a couple of branch circuits and four other subpanels. My house is over 10,000 sf and has 8 panels.
 
Either way wouldn't he have to split it back to 2 separate 200amp breakers after his 400 ATS? Because the feeders (SER, etc.) are longer than tap rules (I assume) and are probably only 3/0 copper or equivalent. I'm just curious how you could put OCPD at 400amps on 3/0 copper.
I thought he was supplying two 200 amp breakers, but if not then yes.

There is no length limitation for outside feeder taps either - but there is rules in 225 about multiple feeders to a separate building/structure to consider, easy way around that though is to parallel them, then it is a 400 amp conductor, and make the taps at the second building/structure.
 
I was thinking similar, why a 400 amp transfer switch then? Why not just do one of the 200A sets?
Cause they potentially need to run "anything" when in standby?

I'd likely suggest similar though - put the more desired loads to have during utility outage on one panel and the rest of the loads in the other panel.
 
But it's not compliant to have a 200A Genny connected to a transfer switch with more than 200 A of load.
right, that why I questioned what is the load earlier? 400 amp breaker doesn't mean there is 400 amp of load, might only be 50 amps for all we know. Chances are it is closer to 200 since OP said it is a 208 amp generator, or there is at least closer to 200 amp of load they do desire to be able to run, but that would require separation or load shedding if on ATS.
 
With the load calculation for the house, a 30kw would work, but they have a shop they want thrown into the mix as well. So currently it's a 320a meter base with triple barrel lugs feeding everything.

The 2 200a panels have main breakers. That being said with 3/0 ran parallel it's good for 400a, but the issue is that it's 3/0 split between 2 separate 200a breakers? What I had initially thought was to feed the 400a service entrance rated ats with 600mcm, then on the load side feed the 2 200a mains with 3/0.

I've only done single 200a services, or when I wired the house one panel was just the circuits the customer wanted to be backed up. Not many people in Texas want to spend money on a backup generator till now.
 
Are the 200a feeds 3-wire service conductors or 4-wire feeders? If the former how hard would it be to make them the latter?
 
With the load calculation for the house, a 30kw would work, but they have a shop they want thrown into the mix as well. So currently it's a 320a meter base with triple barrel lugs feeding everything.

The 2 200a panels have main breakers. That being said with 3/0 ran parallel it's good for 400a, but the issue is that it's 3/0 split between 2 separate 200a breakers? What I had initially thought was to feed the 400a service entrance rated ats with 600mcm, then on the load side feed the 2 200a mains with 3/0.

I've only done single 200a services, or when I wired the house one panel was just the circuits the customer wanted to be backed up. Not many people in Texas want to spend money on a backup generator till now.
That makes them feeder taps, still works just need to comply with 240.21(B). 3/0 on 400 amp is able to use 10 or 25 foot rule. Outdoors has no length limitation.
 