A1b5c0pe1984
Member
- Location
- Ohio
- Occupation
- Electrical Engineer
Hello all,
This is my first post on here, though I have read it many times and it has helped me troubleshoot problems throughout my career. I am currently at the end of my rope on a troubleshooting issue I'm having with a 400A breaker tripping.
This problem has persisted for quite some time. It first showed on an old Motor Control Center (MCC) from probably the 1960s. It was hooked up to an older transformer and would occur periodically over the last two years. The head of maintenance at that location got tired of dealing with it (because when it tripped it would make a giant mess of things in the plant) so he switched the feed of that MCC to a newly installed transformer with a new Main Distribution Panel (MDP) and brand new 400A breakers (hjxd63b400) in hopes that this would fix the problem. It did not and the same thing would occur. It will work for days/weeks/months and heat up and trip. As luck would have it, they are completely redoing this plant and this is when I got involved. In order to redo this plant, we had to get rid of the old MCC in order for us to put one of our new panels in. We already had a Motor Control Panel (MCP) installed because we have done some automation there, with two 400A feeds inside of it. This panel is mostly comprised of FVNR AB starters with E300 overloads on each one. The starters are hung directly on the busbar with a mount that goes to the starter and from there gets passed to the individual motors. When we moved the starters, we split up the trouble MCC from one feed to the other to help try to narrow this down. In doing this we found more problems but that is neither here nor there. Now this issue is showing up on a different breaker in the MDP from when it was hooked up originally as the old MCC.
Things they have tried:
Changing the breaker twice.
Changing the location the breaker is on the MDP.
Megged all leads. Line and motor.
Torqued all fasteners to factory recommendation.
Thermal imaging of the breaker shows the heat originating at the breaker and going to the wires, but gets less hot as the wire leaves the breaker.
Things I have tried:
Put a power analyzer on to check all conditions.
Installed an PowerMonitor 5000 to double check the power analyzer (and store the data).
I was thinking this could be a harmonics issue, but everything that I have recorded tells me it is not.
I am under 3% in all of my harmonic readings.
Current imbalance sits around 3% (have read if you get close to 10% it becomes an issue).
Voltage imbalance is less than .5%.
Power Factor is low around 52% but I wouldn't think that would do this, but I could be wrong.
I am only pulling around 140A continuous on all phases (A phase is a little low, 135A)
I have have been watching A, B and C phase currents from all the motors. The only odd thing I see is a single phase's amps (all A, B or C phase) will jump slightly on all motors at the same time throughout the system. All three phases do this. I don't know if this is a problem or the system correcting itself. Any help would be appreciated.
-Ben
This is my first post on here, though I have read it many times and it has helped me troubleshoot problems throughout my career. I am currently at the end of my rope on a troubleshooting issue I'm having with a 400A breaker tripping.
This problem has persisted for quite some time. It first showed on an old Motor Control Center (MCC) from probably the 1960s. It was hooked up to an older transformer and would occur periodically over the last two years. The head of maintenance at that location got tired of dealing with it (because when it tripped it would make a giant mess of things in the plant) so he switched the feed of that MCC to a newly installed transformer with a new Main Distribution Panel (MDP) and brand new 400A breakers (hjxd63b400) in hopes that this would fix the problem. It did not and the same thing would occur. It will work for days/weeks/months and heat up and trip. As luck would have it, they are completely redoing this plant and this is when I got involved. In order to redo this plant, we had to get rid of the old MCC in order for us to put one of our new panels in. We already had a Motor Control Panel (MCP) installed because we have done some automation there, with two 400A feeds inside of it. This panel is mostly comprised of FVNR AB starters with E300 overloads on each one. The starters are hung directly on the busbar with a mount that goes to the starter and from there gets passed to the individual motors. When we moved the starters, we split up the trouble MCC from one feed to the other to help try to narrow this down. In doing this we found more problems but that is neither here nor there. Now this issue is showing up on a different breaker in the MDP from when it was hooked up originally as the old MCC.
Things they have tried:
Changing the breaker twice.
Changing the location the breaker is on the MDP.
Megged all leads. Line and motor.
Torqued all fasteners to factory recommendation.
Thermal imaging of the breaker shows the heat originating at the breaker and going to the wires, but gets less hot as the wire leaves the breaker.
Things I have tried:
Put a power analyzer on to check all conditions.
Installed an PowerMonitor 5000 to double check the power analyzer (and store the data).
I was thinking this could be a harmonics issue, but everything that I have recorded tells me it is not.
I am under 3% in all of my harmonic readings.
Current imbalance sits around 3% (have read if you get close to 10% it becomes an issue).
Voltage imbalance is less than .5%.
Power Factor is low around 52% but I wouldn't think that would do this, but I could be wrong.
I am only pulling around 140A continuous on all phases (A phase is a little low, 135A)
I have have been watching A, B and C phase currents from all the motors. The only odd thing I see is a single phase's amps (all A, B or C phase) will jump slightly on all motors at the same time throughout the system. All three phases do this. I don't know if this is a problem or the system correcting itself. Any help would be appreciated.
-Ben