JohnDS
Senior Member
- Location
- Suffolk, Long Island
- Occupation
- Electrician
Hey guys,
Just need a refresh here.
400 amp service: 1 meter and 2) 200amp panels located within 5' of meter.
Using 2) 2/0 SEU's going to each panel from meter.
What is the proper way to ground this. This is what I was thinking:
2) #4 solid bear copper grounding electrodes. 1 going from each panel to water main.
2) #6 solid bear copper grounds. 1 going from each panel to it's own ground rod
(2 ground rods total 6'min apart from eachother)
If there is a better way or something wrong here, please let me know. I believe I can use one big grounding electrode and then just jump the panels, but I don't have my book handy. Worse case scenario, would 2 separate #4's be fine?
Just need a refresh here.
400 amp service: 1 meter and 2) 200amp panels located within 5' of meter.
Using 2) 2/0 SEU's going to each panel from meter.
What is the proper way to ground this. This is what I was thinking:
2) #4 solid bear copper grounding electrodes. 1 going from each panel to water main.
2) #6 solid bear copper grounds. 1 going from each panel to it's own ground rod
(2 ground rods total 6'min apart from eachother)
If there is a better way or something wrong here, please let me know. I believe I can use one big grounding electrode and then just jump the panels, but I don't have my book handy. Worse case scenario, would 2 separate #4's be fine?
Last edited: