400a Main breaker fed with 350mcm

Mustang125

Member
Location
New Hampshire
Occupation
Master Electrician, Project Manager and Estimator
See attached image. This is showing a 400a main breaker panel fed with 350mcm, wouldn't this need to be 600mcm by code?
See the attached image showing 350mcm feeding a 400a main breaker panel. This seems like it would need 600mcm by code, wouldn't it?

Electric plans.jpg
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes the conductors are too small. Is the 400 amp "existing main disconnect" the service disconnect with overcurrent protection?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The existing main disconnect is a 400a fused disconnect
So then it looks like the tap rules will apply to the new conductors feeding the nonfused disco from the wireway. Assuming the exiting conductors are 600 they would need to be 600 kcmil since the next size up rule cannot be used.
 

Mustang125

Member
Location
New Hampshire
Occupation
Master Electrician, Project Manager and Estimator
I agree. Not exactly sure. We do see disconnects ahead if its 480v service "hot sequence" and no disconnect before "cold sequence" on 208v. But this is a very old install
Who owns the disconnect? POCO would change things.
We would never see a customer owned disconnect ahead of the meter here.
 

Mustang125

Member
Location
New Hampshire
Occupation
Master Electrician, Project Manager and Estimator
the existing conductors leaving the main disconnect into the wireway where everything is tapping off are 500mcm copper
So then it looks like the tap rules will apply to the new conductors feeding the confused disco from the wireway. Assuming the exiting conductors are 600 they would need to be 600 kcmil since the next size up rule cannot be used.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
the existing conductors leaving the main disconnect into the wireway where everything is tapping off are 500mcm copper
Then 500 kcmil should have been used instead of the 350's and you don't need the non-fused disconnect after the wireway.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
POCO may have supplied and own the secondary conductors. Not your problem. Still wouldn't hurt to ask questions because that new 400 you're putting in lowered the demand. Right?:rolleyes:
I believe he said those are 500's the 350's are feeding the equipment on the right of the diagram
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Then 500 kcmil should have been used instead of the 350's and you don't need the non-fused disconnect after the wireway.
The disconnect after the wireway would allow you to disconnect the far right equipment without shutting the entire service down.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The disconnect after the wireway would allow you to disconnect the far right equipment without shutting the entire service down.
The new panels have a main so the disconnect is redundant and not required. It could be used as you've suggested to completely de-energized the new panels ahead of the main CB.
 