Yes the conductors are too small. Is the 400 amp "existing main disconnect" the service disconnect with overcurrent protection?
The existing main disconnect is a 400a fused disconnect
So then it looks like the tap rules will apply to the new conductors feeding the nonfused disco from the wireway. Assuming the exiting conductors are 600 they would need to be 600 kcmil since the next size up rule cannot be used.The existing main disconnect is a 400a fused disconnect
Who owns the disconnect? POCO would change things.
We would never see a customer owned disconnect ahead of the meter here.
What size fuses are in the disconnect?
So then it looks like the tap rules will apply to the new conductors feeding the confused disco from the wireway. Assuming the exiting conductors are 600 they would need to be 600 kcmil since the next size up rule cannot be used.
Fine due to the next size up rule.id prefer to use 500mcm, it always escapes me when can I
legally use 500mcm for a 400a service when 500mcm is only rated at 380 75degree?
Plus load calculation can not be over 380.Fine due to the next size up rule.
Then 500 kcmil should have been used instead of the 350's and you don't need the non-fused disconnect after the wireway.the existing conductors leaving the main disconnect into the wireway where everything is tapping off are 500mcm copper
I believe he said those are 500's the 350's are feeding the equipment on the right of the diagramPOCO may have supplied and own the secondary conductors. Not your problem. Still wouldn't hurt to ask questions because that new 400 you're putting in lowered the demand. Right?
The disconnect after the wireway would allow you to disconnect the far right equipment without shutting the entire service down.Then 500 kcmil should have been used instead of the 350's and you don't need the non-fused disconnect after the wireway.
The new panels have a main so the disconnect is redundant and not required. It could be used as you've suggested to completely de-energized the new panels ahead of the main CB.The disconnect after the wireway would allow you to disconnect the far right equipment without shutting the entire service down.
the existing conductors leaving the main disconnect into the wireway where everything is tapping off are 500mcm copper
I get 350s to the left of the equipment.I believe he said those are 500's the 350's are feeding the equipment on the right of the diagram
Post 11, OP says they are 500 up to the gutter.I get 350s to the left of the equipment.