400a meter socket 2 outdoor 200a disconnects feeding 2 40 circuit 200a mbp

Status
Not open for further replies.

JoshD

New User
Location
New Hampshire
Occupation
Electrician
So I'm trying to decipher how exactly and what size to run for gec, the setup is parallel 250kcmil aluminum feeding a 240v 400a square d meter socket with a double tapped load side with 4/0 aluminum feeding 2 separate 200a disconnects on the exterior of the house feeding 2 40 circuit 200a mbp panels what I'm trying to figure out is do I have to run 2 separate gec paths and if so what size do they need to be or can I bond all my gec's to say the water pipe and then just run a single 4awg bare to each disconnect

Thank you for your time and sorry if this specific scenario has already been posted I couldn't seem to find it
 
GEC is sized per the largest service conductor, which appears to be 2-250s in parallel effectively making this a 500 kcmil conductor.
 
You have a few options:
Run your GECs from a point ahead of the disconnects such as the meter socket (if your POCO allows)
Run a separate GEC from each disconnect to the Grounding Electrodes
Run a common GEC to the disconnects with a "tap" to each disconnect as shown below:
1699981819450.png
 

Attachments

  • 1699981632151.png
    1699981632151.png
    638.3 KB · Views: 13
Status
Not open for further replies.
Top