I am needing to feed a 400A panel single phase. Would it be better to feed it with 2 sets of 3/0 or one set of 500MCM?
I'm looking at the code book and it says 500 thhn is rated for 430A, has it changed in the new code book?
I'm looking at the code book and it says 500 thhn is rated for 430A, has it changed in the new code book?
Nothing has changed regarding ampacity for decades. You're are looking at the 90° C ampacity. The terminals you're connecting it with are only rated for 75° C so you must use the 75° C ampacity.
So many times I’ve wished manufactures would use 90 degree rated terminals. But alas that shall probably never happen.
If underground, would it not be a wet location? 75C, THWN, 380A
But couldn’t you do this by running the splices outside the breaker boxes to transition from 75 degree to 90 degree for the long run, then back to 75 degree just for the new 400 amp box? Like the video and such I was asking about yesterday! Just butting in, trying to learn better..lol.Not likely to happen any time soon because it's not only the terminals it's also the equipment that the terminals are connected to. The equipment would also need to be designed for use at 90° C. You can buy 90° terminals now but if you slap them on some 75° C equipment you still can only use the conductors at 75° C.