Designer101
- California
- Solar and ESS Designer
Exact comment from plan reviewer.
The line diagram shows that the existing main service panel will be replaced with a new 400A split phase
(200/200) service panel. The panelboard as shown on the line diagram appears to be in violation of CEC
230.71. Panelboards MUST be a type where there is only ONE MAIN breaker in the service panel that
shuts off all other breakers. The new panel CANNOT be a type which has additional breaker slots fed
directly from the utility meter (ie. cannot install a “hot bus” service panel anymore per the 2020 CEC).
Please update the plans to show a service panel with a single service disconnect.