radiopet
Senior Member
- Location
- Spotsylvania, VA
Hey Guys,
I had an AHJ and Guy call me today asking for references for a situation he had so i figured I would run it by you all....found it interesting.
1.) The dwelling has a 400A service ( (2) 200A Panels side by side within the dwelling )
2.) The meter can is being installed on a large board setup about 75' away from the house....so the service latteral will hit a gutter on one side of the board and feed back through to a 400A meter can and a 200A meter can for future garage I think.
3.) The told me that the guy is running (2) 2 inch PVC Sch 80 from the meter to the panels located inside the dwelling....again 75' away...but once inside the house will only go about 3 feet so it is at the point of entrance of the actual dwelling where the panels are located.
Now.......here was the question.....and while I felt it was clear I now question it so i ask you guys as well...
A.) he allowed the guy to use 310.15(b)(6) to size each (set) of 3 conductors to each 200A panel in its own 2" PVC conduit.
However it would appear 310.16 is the determineing table here....
Anyway he allowed (2) 2" conduits to hold (3) 2/0Cu Conductors and one conduit went to each 200A panel inside the dwelling.
To me 310.15.b.5 MAY apply to only (1) set of service enterance conductors.....yet we see all the time a 400A meter can with (2) 200A panels on the other side of the wall and fed from (2) different 4/0 AL SE cable...
While again we see this all the time......does this not confuse the application of 310.15(b)(6)
Any thoughts guys.....
I had an AHJ and Guy call me today asking for references for a situation he had so i figured I would run it by you all....found it interesting.
1.) The dwelling has a 400A service ( (2) 200A Panels side by side within the dwelling )
2.) The meter can is being installed on a large board setup about 75' away from the house....so the service latteral will hit a gutter on one side of the board and feed back through to a 400A meter can and a 200A meter can for future garage I think.
3.) The told me that the guy is running (2) 2 inch PVC Sch 80 from the meter to the panels located inside the dwelling....again 75' away...but once inside the house will only go about 3 feet so it is at the point of entrance of the actual dwelling where the panels are located.
Now.......here was the question.....and while I felt it was clear I now question it so i ask you guys as well...
A.) he allowed the guy to use 310.15(b)(6) to size each (set) of 3 conductors to each 200A panel in its own 2" PVC conduit.
However it would appear 310.16 is the determineing table here....
Anyway he allowed (2) 2" conduits to hold (3) 2/0Cu Conductors and one conduit went to each 200A panel inside the dwelling.
To me 310.15.b.5 MAY apply to only (1) set of service enterance conductors.....yet we see all the time a 400A meter can with (2) 200A panels on the other side of the wall and fed from (2) different 4/0 AL SE cable...
While again we see this all the time......does this not confuse the application of 310.15(b)(6)
Any thoughts guys.....
Last edited: