DST83
Member
- Location
- Hannibal, Missouri
We are working on a job where the prints call out for us to install a 480/277V 400A breaker to be fed by (4) #400MCM THHN/THWN conductors and (1) #4 ground. The feed from the breaker goes to a 480/277V 130kVA UPS with an input voltage of 151A. The UPS then feeds a 480/277V 300A panel which feeds a 480-120/208V 45kVA transformer which then feeds another 208/120V 150A panel.
The question here is whether or not the (4) #400MCM conductors is sufficient as the feeder from the 400A breaker to the UPS. By the code table it does not appear to be but (and not to be caddy) this was engineered for a reason the way it is, we just can't figure out why and if it will really meet NEC code.
Any advice?
Thanks -
The question here is whether or not the (4) #400MCM conductors is sufficient as the feeder from the 400A breaker to the UPS. By the code table it does not appear to be but (and not to be caddy) this was engineered for a reason the way it is, we just can't figure out why and if it will really meet NEC code.
Any advice?