400amp service fused disconnect

Status
Not open for further replies.

dcsva@aol.com

Senior Member
Location
Virginia
This is the bottom half of a 277/480VAC service disconnect with 400amp fuses. I was looking at this to see what size fuses were installed and this is what I saw.
Aside from all the tobacco dust, they crammed 3 wires under each phase load lug rated for only 2 conductors.
Any opinions out there about the load ground connection on the right side of the cabinet?
The lower picture zooms in on the load grounds.

FD400a.jpg


FD400gnda.jpg
 

charlie

Senior Member
Location
Indianapolis
Re: 400amp service fused disconnect

I assume this was dead when you took the picture and you have declined working around this place? This is obviously a Class II, Div 1 location and the whole area needs to be rewired. If you haven't already, run and don't look back. :D
 

dcsva@aol.com

Senior Member
Location
Virginia
Re: 400amp service fused disconnect

Charlie,
The picture of this switch shows the results of a NEMA-1 enclosure in a NEMA-12 environment after 10 years.
All other enlosures in this area are NEMA-12 and look brand new inside (zero dust), why this one is NEMA-1 is a question and it should be replaced.
 