faresos

Senior Member
Hello Everyone:

I'm working on a project (Avionics) where the client is requesting a 120V-single phase and 120Y-3-phase. I'm a little confuse with the 120Y-3-Phase terminology, do they mean 208Y-3-phase? is there anything such 120Y-3-phase in the 400HZ power distribution world? I looked at the existing facility and the 3-phase circuit is fed from 3-poles breaker.

Thanks,
 

drcampbell

Senior Member
Location
The Motor City, Michigan USA
Occupation
Registered Professional Engineer
I'm sure that's what they mean: three phases, each of which is 120 volts to the common center tap.

Most of the 400-Hz aircraft circuits I've seen have been 115Y200 volts, but I doubt the distinction is terribly significant.
 

kwired

Electron manager
Location
NE Nebraska
Most likely is three 120 volt coils connected in wye and has 208 between outer ends.

No experience in these applications - may be possible there just isn't any loads that operate at 208 volts and they simply refer to it as a 120 volt source because all loads are 120 volts?
 