Dear Experts
A year ago my american friend ask me about the electrical system of a 30 story condo.His business partners are planning to put it near a beach in Thailand.Since I worked there for quite sometime, they ask me for my recommendation.
1.The Utility practice there is that all energy meter is at ground floor,(otherwise its a private meter if located per floor and utility will have main meter at transformer secondary, building admin will bill the occupants)
2. All service above 500KVA, Client will have to give 60% deposit for service transformers to be deducted on billings for 10 years. Secondary Voltage is per client request.
My recommendation to him is the following.
3. Use utility metering so that Building admin will not bother itself with billing the occupants.This mean that each Unit feeder will run down to the Utility meter room.
a. I suggest to use the 400V 3PH 4W distribtion voltage, with 230V L-N as utilization voltage, central split-AC for each units can use the 400V 3ph.
this will give maximum savings on materials such as feeder wires,( higher load capacity for same size of wire, lower power loss due to voltage drop. this is the point that I'm stressing on using 400V for a 600V wire instead of 230V, while both are safe.) smaller breaker ratings,
b. All lightings and appliances are on 230V, this is the normal voltage here, and I think on other asian countries as such as Japan, Singapore. and that no shock fatalities have been of significant occurences on these countries using this voltage.
c. With a single voltage, Universal type ( can accept pin or blade plugs) receptacles can be used, all nema plug types except locking can be used.
d. The percent impedance for a distribution type Padmouted Transformer (used by Utility ) is the same for 400 or 230V secondary at same KVA. So the fault duty is smaller for 400V dist.voltage. Also cascade ratings can be applied for branch CB's since this is mostly lighting & receptacle loads. Industrial type CB's are not necessary.
e. For wiring method I suggested the used of Cu-XLPE-PVC multicore cable (also common here ) feeder run on vertical cable trays. The NEC being mentioned here but as a guide only.
If things push through I may be the have to design the plan for this, they are already processing the acquisition of the property. A friend told me that this is voltage system is not approved in the US.
My question now is why is the 400V 3ph 4W / 230V L-N is not allowed by the NEC for residential occupancies? What are they afraid of ? If ever this is allowed by NEC will the Utility provide this voltage?
DavidV
Electrical Supervisor
A year ago my american friend ask me about the electrical system of a 30 story condo.His business partners are planning to put it near a beach in Thailand.Since I worked there for quite sometime, they ask me for my recommendation.
1.The Utility practice there is that all energy meter is at ground floor,(otherwise its a private meter if located per floor and utility will have main meter at transformer secondary, building admin will bill the occupants)
2. All service above 500KVA, Client will have to give 60% deposit for service transformers to be deducted on billings for 10 years. Secondary Voltage is per client request.
My recommendation to him is the following.
3. Use utility metering so that Building admin will not bother itself with billing the occupants.This mean that each Unit feeder will run down to the Utility meter room.
a. I suggest to use the 400V 3PH 4W distribtion voltage, with 230V L-N as utilization voltage, central split-AC for each units can use the 400V 3ph.
this will give maximum savings on materials such as feeder wires,( higher load capacity for same size of wire, lower power loss due to voltage drop. this is the point that I'm stressing on using 400V for a 600V wire instead of 230V, while both are safe.) smaller breaker ratings,
b. All lightings and appliances are on 230V, this is the normal voltage here, and I think on other asian countries as such as Japan, Singapore. and that no shock fatalities have been of significant occurences on these countries using this voltage.
c. With a single voltage, Universal type ( can accept pin or blade plugs) receptacles can be used, all nema plug types except locking can be used.
d. The percent impedance for a distribution type Padmouted Transformer (used by Utility ) is the same for 400 or 230V secondary at same KVA. So the fault duty is smaller for 400V dist.voltage. Also cascade ratings can be applied for branch CB's since this is mostly lighting & receptacle loads. Industrial type CB's are not necessary.
e. For wiring method I suggested the used of Cu-XLPE-PVC multicore cable (also common here ) feeder run on vertical cable trays. The NEC being mentioned here but as a guide only.
If things push through I may be the have to design the plan for this, they are already processing the acquisition of the property. A friend told me that this is voltage system is not approved in the US.
My question now is why is the 400V 3ph 4W / 230V L-N is not allowed by the NEC for residential occupancies? What are they afraid of ? If ever this is allowed by NEC will the Utility provide this voltage?