I was reading another thread about a 400Y/230 volt transformer. I have never heard of this system voltage before. Is it common and in what types of installations?
In UK, the distribution transformer is often 11kV delta primary and the secondary ia star 400VLL and 230VLNI was reading another thread about a 400Y/230 volt transformer. I have never heard of this system voltage before. Is it common and in what types of installations?
Yes, the UPS mfrs are pushing this concept because they want to control more of the power distribution chunk by making UPS systems that take in 480V and put out 415Y240V without the need for an external transformer. Using 240V to feed single phase server power supplies increases the power density of the distribution system (vs 120V).There has been some traction to using 415/240V 3 phase in data centers, since most computer power supplies are rated to handle 240V.
http://www.missioncriticalmagazine....ome/Files/PDFs/Emerson-Proper_Application.pdf