[quote: Q16 When is the neutral conductor required to be provided at the switch location for lighting loads?
A16 Switches controlling line-to-neutral lighting loads must have a neutral provided at the switch location [404.2(C)] unless either of the conditions of the following exception are met.
Ex: The neutral conductor isn?t required at the switch location if:
(1) The conductors for switches enter the device box through a raceway that has sufficient cross-sectional area to accommodate a neutral conductor. Figure 404?1
(2) Cable assemblies for switches enter the box through a framing cavity that?s open at the top or bottom on the same floor level, or through a wall, floor, or ceiling that?s unfinished on one side. Figure 404?2
Note: The purpose of the neutral conductor is to complete a circuit path for electronic lighting control devices. end quote:]
I hope the NEC Handbook explains this one. Exception 1. is missing the phrase "does not" I believe, and Exception 2. is difficult to comprehend.
A16 Switches controlling line-to-neutral lighting loads must have a neutral provided at the switch location [404.2(C)] unless either of the conditions of the following exception are met.
Ex: The neutral conductor isn?t required at the switch location if:
(1) The conductors for switches enter the device box through a raceway that has sufficient cross-sectional area to accommodate a neutral conductor. Figure 404?1
(2) Cable assemblies for switches enter the box through a framing cavity that?s open at the top or bottom on the same floor level, or through a wall, floor, or ceiling that?s unfinished on one side. Figure 404?2
Note: The purpose of the neutral conductor is to complete a circuit path for electronic lighting control devices. end quote:]
I hope the NEC Handbook explains this one. Exception 1. is missing the phrase "does not" I believe, and Exception 2. is difficult to comprehend.