404.22 in 2023 code. Violation?

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Saw this interesting new product that looks like it violates the code. It is advertising grounding the neutral conductor if there is no neutral present in the switch location.

 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Amazing they pushed for AFCI/GFCI for so many installations and then they allow and make an exception for a device that would make nuisance tripping a greater issue. The information being provided by the mfg. doesn't give the neutral current being sent by the device's electronics, that it is being suggested would be allowed.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
A few years back i had a weird service call where people were felling a shock from both the bathrooms in a old office building and the lights were not working reliably.
Turned out maintenance had installed occupancy sensors everywhere that used the EGC as a grounded conductor like these devices do. And the older EMT and BX cable was the ground path, no wire type egc in that era. One on a circuit probably would have been fine but this building had like 5-10 sensors per circuit.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Turned out maintenance had installed occupancy sensors everywhere that used the EGC as a grounded conductor like these devices do. And the older EMT and BX cable was the ground path, no wire type egc in that era. One on a circuit probably would have been fine but this building had like 5-10 sensors per circuit.
Is this a case of the BX cable armor being a high resistance ground, so if the occupancy sensors are sinking a basically fixed current into the EGC, the resulting voltage drop is higher than with a proper EGC, causing enough voltage difference to provide a sensible shock?

Cheers, Wayne
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Is this a case of the BX cable armor being a high resistance ground, so if the occupancy sensors are sinking a basically fixed current into the EGC, the resulting voltage drop is higher than with a proper EGC, causing enough voltage difference to provide a sensible shock?

Cheers, Wayne
Given the product standard limit of 0.5mA for the current on the equipment grounding conductor for this type of equipment, there would not be much voltage drop. The bigger issue is where the EGC is open and you get between that and a path to ground where you will get a line voltage shock, but at a very low current.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Given the product standard limit of 0.5mA for the current on the equipment grounding conductor for this type of equipment, there would not be much voltage drop.
There is no limit to how many of these can be on a branch circuit.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Given the product standard limit of 0.5mA for the current on the equipment grounding conductor for this type of equipment, there would not be much voltage drop. The bigger issue is where the EGC is open and you get between that and a path to ground where you will get a line voltage shock, but at a very low current.
Don, what was the standard permitted amount current on the EGC before neutrals were required at certain switch locations?
 
Top