Dark Sparky
Member
- Location
- USA
- Occupation
- Electrical Engineer
An owner wants to install a disconnect for some HVAC equipment - high up on a wall (perhaps 12+ feet). It is unclear whether this disconnect may be accessible from the HVAC equipment's platform.
1) If accessible from the platform, I assume NEC 2020 404.8, Exception 2 applies ("Switches and circuit breakers installed adjacent to motors, appliances, or other equipment that they supply shall be permitted to be located higher than 2.0m (6' 7") and to be accessible by portable means."). (In this case, portable means would not even be required.) Correct that this would be permissible?
2) If not accessible from the platform (in other words, if the disconnect's position on the wall is too far away from the platform to reach), does 404.8 Exception 3 apply? Exception 3 reads: "Hookstick operable isolating switches shall be permitted at greater heights." I am not certain how long the hooksticks practically can be (it seems a 10' hookstick for example, might invite AHJ commentary?). Also - I am not certain I understand the intent of the NEC definition of an isolating switch: "A switch intended for isolating and electrical circuit from the source of power. It has no interrupting rating, and it is intended to be operated only after the circuit has been opened by some other means." Is that definition intended to include simple non-fusible disconnects like we have here?
Thanks in advance - love the interaction on this forum!
1) If accessible from the platform, I assume NEC 2020 404.8, Exception 2 applies ("Switches and circuit breakers installed adjacent to motors, appliances, or other equipment that they supply shall be permitted to be located higher than 2.0m (6' 7") and to be accessible by portable means."). (In this case, portable means would not even be required.) Correct that this would be permissible?
2) If not accessible from the platform (in other words, if the disconnect's position on the wall is too far away from the platform to reach), does 404.8 Exception 3 apply? Exception 3 reads: "Hookstick operable isolating switches shall be permitted at greater heights." I am not certain how long the hooksticks practically can be (it seems a 10' hookstick for example, might invite AHJ commentary?). Also - I am not certain I understand the intent of the NEC definition of an isolating switch: "A switch intended for isolating and electrical circuit from the source of power. It has no interrupting rating, and it is intended to be operated only after the circuit has been opened by some other means." Is that definition intended to include simple non-fusible disconnects like we have here?
Thanks in advance - love the interaction on this forum!