404.9 (B) question

Status
Not open for further replies.

POWER_PIG

Senior Member
Hi Folks! I have question concerning installing a regular 15a switch in a surface mounted 4 square and using an industrial / RS type metal cover. Does 404.9 ( B) mean I don't have attach an actual bond wire to the switch yoke?

Thanks,
Pig
 

resistance

Senior Member
Location
WA
<><><><><>
I 'm on page with the others!

To add, I feel it's best to attach the EGC to the device.
 
Last edited:

POWER_PIG

Senior Member
Very prompt response! another reason I love this forum, and thanks. I thought that was to be true, but was asked today by another electrician and wanted to make sure I wasn't steering him in the wrong direction.

thanks again,
Pig
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Switches do not required a bonding jumper for these types of covers. Receptacles won't require them either under the 2008 code if the cover has indented corners like a cover for a 1900 box.
 

peter d

Senior Member
Location
New England
Thanks for the '08 code info. But I never installed a bonding jumper for switches on raised covers anyway. At least now it's code legal. ;)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
iwire said:
They do under the 2005 NEC.


Do you mean receptacles? That's true, since those types of covers are already listed for bonding the device. The new code verbiage spells it out directly. Saves someone the time looking up the listing of the specific cover.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
iwire said:
No I mean for switches, 404.9(B) requires that metal face plate to be grounded.


I can see your argument for the bonding jumper but the switch is grounded to the box by the cover mounting screws. The requirement is for the cover to be grounded and the cover mounting screws provide this function. This is really not much different from mounting a switch to a mud ring.
 

iwire

Moderator
Staff member
Location
Massachusetts
Rob, Read (1) to 409.4(B) and notice that only applies to switches mounted to boxes (like a mud ring) not mounted to covers.

A switch mounted to a raised cover has to have a wire EGC running to it.
 

stickboy1375

Senior Member
Location
Litchfield, CT
iwire said:
Rob, Read (1) to 409.4(B) and notice that only applies to switches mounted to boxes (like a mud ring) not mounted to covers.

A switch mounted to a raised cover has to have a wire EGC running to it.

Bob, not that I disagree with you, but they allow a receptacle to to be installed in a raised cover without a pigtail, so why in the world would a switch not be allowed?
 

iwire

Moderator
Staff member
Location
Massachusetts
stickboy1375 said:
but they allow a receptacle to to be installed in a raised cover without a pigtail, so why in the world would a switch not be allowed?


No one has put in a proposal that made it?
 

stickboy1375

Senior Member
Location
Litchfield, CT
iwire said:
No one has put in a proposal that made it?

Thats what I was thinking...

Here is a pic for what 404.9(B)(1) is actually saying, for anyone following along at home.. :) Personally, I dont see much difference in a mud ring vs a raised cover as far as bonding is concerned.

408ecm31fig1.jpg
 
Last edited: