Hi.
A student in class right now suggests that a hand held GFCI receptacle tester will not cause the GFI to trip unless you jumper the neutral to the ground when replacing a two wire receptacle with a GFCI receptacle. No equipment ground is present.
I advised the student that making this jumper would be a violation of 250-24(A)(5) even though the equipment grounding conductor is not present an unintentional path to ground could be created depending on conditions of installation.
Anyone else run into this? I have not personally tried to test a 2 wire replacement this way. Advice? Input?
thanks.
A student in class right now suggests that a hand held GFCI receptacle tester will not cause the GFI to trip unless you jumper the neutral to the ground when replacing a two wire receptacle with a GFCI receptacle. No equipment ground is present.
I advised the student that making this jumper would be a violation of 250-24(A)(5) even though the equipment grounding conductor is not present an unintentional path to ground could be created depending on conditions of installation.
Anyone else run into this? I have not personally tried to test a 2 wire replacement this way. Advice? Input?
thanks.