A long time ago someone told me that using a bonding jumper from a metal box to a receptacle was required because the plaster ring or raised industrial cover isn't listed as part of the equipment grounding conductor. I was reading in the switch part of the nec (2014) and it explicitly allows this, so I figured I'd just look at the same code number for the receptacles and read similar verbage. I'm then directed to 250.1469(A) which allows using the screw to bond as long as there is good contact between the box and the yoke but not there is a cover used unless "the box and cover combination are listed as providing satisfactory ground continuity between the box and the receptacle."
The question is, are there any box cover combinations that are listed as satisfactory?