This is one of the topics that was discussed in a 2011 NEC Changes class I took a few weeks ago and I brought it up during our monthly local contractor's association meeting tonight. As was explained in class, beginning in 2014 cycle, if you change a receptacle device, that circuit must be brought up to code using any of the proposed methods below, meaning some means of AFCI protection must now be installed. Is that the correct assessment? Some were in disagreement this evening. It is how I read it. How about you?
Some said it only applied to receptacles that were already required to have AFCI, not to 10+ year old circuits that were not required at the time, enabling a swap out. It seems to me that if it was already on a required AFCI circuit than this section would be redundant.
406.4 (D)
(4) Arc-Fault Circuit-Interrupter Protection. Where a
receptacle outlet is supplied by a branch circuit that requires
arc-fault circuit interrupter protection as specified
elsewhere in this Code, a replacement receptacle at this
outlet shall be one of the following:
(1) A listed outlet branch circuit type arc-fault circuit interrupter
receptacle
(2) A receptacle protected by a listed outlet branch circuit
type arc-fault circuit interrupter type receptacle
(3) A receptacle protected by a listed combination type
arc-fault circuit interrupter type circuit breaker
This requirement becomes effective January 1, 2014.
(I highlighted in blue what I think to be the key phrase.)
Some said it only applied to receptacles that were already required to have AFCI, not to 10+ year old circuits that were not required at the time, enabling a swap out. It seems to me that if it was already on a required AFCI circuit than this section would be redundant.
406.4 (D)
(4) Arc-Fault Circuit-Interrupter Protection. Where a
receptacle outlet is supplied by a branch circuit that requires
arc-fault circuit interrupter protection as specified
elsewhere in this Code, a replacement receptacle at this
outlet shall be one of the following:
(1) A listed outlet branch circuit type arc-fault circuit interrupter
receptacle
(2) A receptacle protected by a listed outlet branch circuit
type arc-fault circuit interrupter type receptacle
(3) A receptacle protected by a listed combination type
arc-fault circuit interrupter type circuit breaker
This requirement becomes effective January 1, 2014.
(I highlighted in blue what I think to be the key phrase.)