406.4(D)

Status
Not open for further replies.

arnettda

Senior Member
406.4(D)(2)(b) says I can replace a two prong outlet with a GFCI. Can I replace a old two prong outlet in a bathroom with a GFCI? It does not say that exactly and am working on a home inspectors report for a realtor.
Thank You
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes, the replacement is the same for locations that actually require GFCI protection.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Each such receptacle needs to be GFCI protected, not necessarily GFCI receptacles. Also remember to NOT connect any EGC to such replacements, so one malfunctioning device does not energize another.
 