I'm hoping i can get some help here, I'm new to residential so some of the code is foreign to me. The new NEC changed some wording in 406.9(C) to now read:
"(C) Bathtub and Shower Space.
Receptacles shall not be installed inside of the tub or shower or within a zone measured 900 mm (3 ft) horizontally from any outside edge of the bathtub or shower stall, including the space outside the bathtub or shower stall space below the zone.
The zone also includes the space measured vertically from the floor to 2.5 m (8 ft) above the top of the bathtub rim or shower stall threshold. The identified zone is all-encompassing and shall include the space directly over the bathtub or shower stall and the space below this zone, but not the space separated by a floor, wall, ceiling, room door, window, or fixed barrier."
I'm focusing on the last sentence there. I have a his/her sink going up with two basins, and one is up against the pony wall because the mirror is in the way as i face the basin. instinctively i want to put the receptacle against the pony wall, but 2020 code prohibited it because of that 3 ft space from the tub, does this new code now allow me to?
Also, as i mentioned, new to residential, if I'm not allowed against that pony wall, where is a good location for the receptacle serving that basin? what are your recommendations?
thank you for any help and input you may offer
"(C) Bathtub and Shower Space.
Receptacles shall not be installed inside of the tub or shower or within a zone measured 900 mm (3 ft) horizontally from any outside edge of the bathtub or shower stall, including the space outside the bathtub or shower stall space below the zone.
The zone also includes the space measured vertically from the floor to 2.5 m (8 ft) above the top of the bathtub rim or shower stall threshold. The identified zone is all-encompassing and shall include the space directly over the bathtub or shower stall and the space below this zone, but not the space separated by a floor, wall, ceiling, room door, window, or fixed barrier."
I'm focusing on the last sentence there. I have a his/her sink going up with two basins, and one is up against the pony wall because the mirror is in the way as i face the basin. instinctively i want to put the receptacle against the pony wall, but 2020 code prohibited it because of that 3 ft space from the tub, does this new code now allow me to?
Also, as i mentioned, new to residential, if I'm not allowed against that pony wall, where is a good location for the receptacle serving that basin? what are your recommendations?
thank you for any help and input you may offer