408.16(B)
In addition to the requirements of 408.13, a power panelboard with supply conductors that include a neutral and having more than 10 percent of its overcurrent devices protecting branch circuits rated 30 amperes or less shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard.
Does this mean that if there is no neutral (or if there is less than 10 percent of OCPDs 30 amperes or less) then the panelboard does not need to be protected by an OCPD. (This question is about a regular panel, not one used as service equipment.)
I seem to be having a brain lock on this, and it doesn't seem to make sense.
In addition to the requirements of 408.13, a power panelboard with supply conductors that include a neutral and having more than 10 percent of its overcurrent devices protecting branch circuits rated 30 amperes or less shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard.