Situation... 120/240V Delta 3-phase system from POCO. They don't have the means to provide 120/208.
Many times I have seen existing 3-phase delta panels with the "High Leg" on the "A" or "C" phase lug. 408.3E1 tells me that I have to arrange the phases "A, B, C" left to right, and that the "B" phase shall have the higher voltage to ground. Then 408.3F1 tells me I need to mark the panel... " Caution ____ Phase Has ____ Volts to Ground."
Not meeting the exception in E1... Why would they tell you that the "B" phase in the high leg, then give you the option as to which phase has what volts to ground? I have seen it many times where either "A" or "C" phase are marked as the High leg in the panel.
Many times I have seen existing 3-phase delta panels with the "High Leg" on the "A" or "C" phase lug. 408.3E1 tells me that I have to arrange the phases "A, B, C" left to right, and that the "B" phase shall have the higher voltage to ground. Then 408.3F1 tells me I need to mark the panel... " Caution ____ Phase Has ____ Volts to Ground."