408.4 (B) Source of Supply
tom baker
First Chief Moderator
This new rule requires the source of supply to be marked on switchboards and panelboards.
But the rules does not apply to fused switches, which are in Art 404. Was that an oversight or intentional?
Considering a code proposal.
bluesmoke...oops
The way I see it, it's to make it so you can tell right away where a panel is being fed from. Probably to help stop having to just start turning things off until you find the source.
I think the fused switch is being treated as more of a branch circuit application and not a feeder.
When it comes to having to do renovations, I would like to see labels on everything, but I know that's not going to happen.
tom baker
This rule in 408 would not apply to a common application, for HVAC rooftop units....if they use fused disconnects
marti smith
After reading the commentary on why it was revised, it appears that it is an oversight for fuses, as the premise of the reasoning relates to fuses (fused disconnects) in the same manner as it does to switchboards and panelboards, but yet they are in fact not included.