eric9822
Senior Member
- Location
- Camarillo, CA
- Occupation
- Electrical and Instrumentation Tech
We are in the early stages of a turnkey industrial control system replacement project. The vendor is supplying all the I/O enclosures and is building them to comply with UL 508A. They have asked us if we need to actually have them listed and "stickered" because they did not plan on supplying drawings as required, only termination lists. Our initial thought was maybe not since our AHJ does not typically require UL listing for this sort of thing as long as the components are UL listed. While researching the issue I also re-read 409.110 which states (amongst other things):
409.110 Marking. An industrial control panel shall be
marked with the following information that is plainly visible
after installation:
(5) Electrical wiring diagram or the number of the index to
the electrical drawings showing the electrical wiring
diagram.
At that point I said UL508A "stickering" may not be required but since you need to supply drawings anyway and you are building them in a UL panel shop you might as well apply the stickers. The vendor replied they have no plans to provide drawings and the electrical termination lists are equivalent. I disagree since the code does not state drawings or equivalent. Am I seeing this correctly?
409.110 Marking. An industrial control panel shall be
marked with the following information that is plainly visible
after installation:
(5) Electrical wiring diagram or the number of the index to
the electrical drawings showing the electrical wiring
diagram.
At that point I said UL508A "stickering" may not be required but since you need to supply drawings anyway and you are building them in a UL panel shop you might as well apply the stickers. The vendor replied they have no plans to provide drawings and the electrical termination lists are equivalent. I disagree since the code does not state drawings or equivalent. Am I seeing this correctly?