I was on a job today and as I was leaving the HO asked me to look at her free standing range. She told me that when she turns on the burners and the oven the breaker trips. I looked at the panel, outdoor FPE, and noticed that the range was on a 30A breaker with #10.
Just for kicks and giggles I put a meter on the circuit at the panel and turned on every burner and the oven. I read anywhere between 42 and 45A. The name plate says it's 12.5kW.
My question: How should I size the new wiring for this unit? I've looked at Table 220.55 and done the math but the meter readings tell me differently.
Could the current wire size, 10's, give me a higher reading?
Thanks