Looking at appliance cuts this morning, very fun. (Yeah right.) We are installing a GE range. Says "Breaker size: 40A". Says "kW rating: 10.7 @ 208V". Do the math...
10700 VA / 208V = 51.4A. That's bigger than the breaker.
A 40A breaker is good for 40A * 208V *0.8 = 6656 VA. Am I correct it is fair to use this smaller number in the load calculations?